[Op1st-dc-alerts] [mghpcc-alerts] Update **Potentially Service-Affecting** Electrical Work December 12-17, 2022
mghpcc-alerts at mghpcc.org
mghpcc-alerts at mghpcc.org
Mon Dec 12 18:06:29 EST 2022
The switchboard that was powered down this morning will be
powered up again on Tuesday morning at approximately 9AM.
30 minutes later, the second switchboard involved in the construction
activity will be powered down.
Apologies for publishing an incorrect list of affected pods. The areas
affected today and tomorrow are:
Pods
R6-PA
R6-PB
R6-PC
Entrance Rooms
ER-01
ER-02
We will update tomorrow with additional information about activities
planned for the rest of the week.
======= December12, 2022 Alert ==========
The first of the four switchboards involved in the construction activity
was powered down at approximately 8:30 this morning. In addition
to the pods called out in the November 30 and December 7 alerts,
this affected the two MGHPCC Entrance Rooms. Apologies for not
making that clear in the earlier alerts.
The Comcast modems that support management connections for
some of you are single-corded, and went down for a brief period
while we switched them over to the alternate feed.
We are also aware of two network devices that appear to have
been affected by loss of one of the two redundant power feeds.
The networking organizations that maintain those devices will
communicate status as needed.
======= December 7, 2022 Alert ==========
Notice of two upcoming events that have the potential to affect service.
1. Plan to power down the switchboards that feed power to the following
Pods in the MGHPCC computer room at different times during the week
of December 12, 2022.
R1-PA,
R1-PB (even side)
R2-PA, R2-PB
R3-PA (even side)
R4-PA (even side)
R5-PB
2. Generator maintenance on December 15 and 16, 2022.
All work will take place between 7AM and 6PM.
Tenant Impact
--------------------
There may be brief periods of time when we will ask everyone to leave the
Computer Room for safety (e.g. when a switchboard is being powered up).
Computing, Storage, and Networking equipment in the pods listed above
that has been properly configured for operation with power cords attached
to both the “A” and “B” PDUs in their racks should not be affected.
Equipment in pods other than the ones listed above should not be affected,
independent of configuration.
There is elevated risk for the entire Computer Room while the work is
being done.
Description
—————
The switchboards that feed power to the pods listed above will be powered
down to install new electrical circuits in the MGHPCC computer room. The
switchboards will be powered down one at a time, so there will always be at
least one bus with active power in every pod. Each of the four switchboards
involved in this work will be powered down for approximately two days.
MGHPCC will be performing routine preventive maintenance on the two generators
in the transformer yard. This will involve disabling each generator while the maintenance
work is being done. In the unlikely event that a utility power outage occurs while one
of the generators is unavailable, operation of both UPS-backed and non-UPS-backed
equipment in the data center would be disrupted.