[Op1st-dc-alerts] [mghpcc-alerts] Update re: MGHPCC Utility Power outage Saturday October 14 at 4:33PM CCF23667273

Crown Castle Fiber NOC fibersupport at crowncastle.com
Sat Oct 14 21:18:21 EDT 2023


+ CCF23667273

Michael Mackley
NOC Technician II
T: (855) 93-FIBER
CROWN CASTLE FIBER
fibersupport at crowncastle.com
Fiber.CrownCastle.com

-----Original Message-----
From: mghpcc-alerts <mghpcc-alerts at mghpcc.org>
Sent: Saturday, October 14, 2023 9:01 PM
To: mghpcc-alerts <mghpcc-alerts at mghpcc.org>
Subject: [mghpcc-alerts] Update re: MGHPCC Utility Power outage Saturday October 14 at 4:33PM

[You don't often get email from mghpcc-alerts at mghpcc.org. Learn why this is important at https://aka.ms/LearnAboutSenderIdentification ]

Update: Saturday October 14 at 9:00PM
--------------------------------------------
Based on feedback received, we will:
   Bring Entrance Room power up now
   Bring Computer Room power up Sunday morning at 8AM


Update: Saturday October 14 at 7:30PM
--------------------------------------------
Power-on sequence has started.
We will be restoring power to the Entrance Rooms at approximately 7:40PM

Please send mail to help at mghpcc.org if you see current or prospective issues as power comes back.


Update: Saturday October 14 at 7:29PM
--------------------------------------------
HG&E has restored its power feed.
We are starting the power-on sequence for the data center.

Power will be restored in stages.

Update: Saturday October 14 at 6:10PM
--------------------------------------------

We have confirmed that power to UPS-backed systems in the Computer Room and Entrance Rooms is down.

Immediate steps under way are:
(1)     Make sure it's OK to restore utility power.
(2)     Send an alert warning that utility power is about to be restored.
    (2) Restore utility power.

Follow up steps:
    (3) Root cause the problem the prevented generator power from reaching UPS-backed
         racks in the computer room and ERs.
    (4) Stay in touch with HG&E as they root cause the reasons why the North Canal
         Substation went down when a fault occurred there, instead of failing over to a
         redundant circuit.



Saturday October 14 at 4:33PM
-----------------------------------

The primary utility power feed to the MGPCC facility was interrupted at 4:33PM today (October 14, 2023).

UPS-backed power may have been affected.

We will provide updates as we make progress toward restoring power via the backup power feed.